⟦f162e11d7⟧ Wang Wps File

    Length: 25423 (0x634f)
    Types: Wang Wps File
    Notes: CPS/SDS/001  ISSUE 1      
    Names: »0682A «

Derivation

└─⟦6472223e8⟧ Bits:30006010 8" Wang WCS floppy, CR 0045A
    └─ ⟦this⟧ »0682A « 

WangText



…08……08……08……0b……08……0c……08……0d……08…
…07……08……07……0d……07……0e……07……0f……07…    …86…1
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     
     …02…
     
     
     
     
     
    …02… 
     …02…
     
     
     
     


…02…CPS/SDS/001

…02…HKI/810430…02……02…
CAMPS
 SYSTEM
 DESIGN
 SPECIFICATION
…02…ISSUE
 1…02…CAMPS









                 T̲A̲B̲L̲E̲ ̲O̲F̲ ̲C̲O̲N̲T̲E̲N̲T̲S̲



     5.7  IO CONTROL SOFTWARE PACKAGE .............. 
     312
       5.7.1  Summary of Requirement ............... 
       312
         5.7.1.1  Package Description .............. 
         312
           5.7.1.1.1  Summary of Function .......... 
           315
           5.7.1.1.2  Summary of External Interfaces 
           317

         5.7.1.2  Package Functions ................ 
         320
           5.7.1.2.1  Line Interface Control ....... 
           320
           5.7.1.2.2  Device and Line Control ...... 
           332

         5.7.1.3  Package Control .................. 
         345
         5.7.1.4  Characteristics .................. 
         346
         5.7.1.5  Design and Construction .......... 
         346
         5.7.1.6  Documentation .................... 
         346

       5.7.2  Environment .......................... 
       346
         5.7.2.1  Standard Hardware, Firmware, and
                  Software ......................... 
                 346
         5.7.2.2  External Interfaces .............. 
         346
         5.7.2.3  Subsystem Interfaces ............. 
         346



5.7      I̲O̲ ̲C̲O̲N̲T̲R̲O̲L̲ ̲S̲O̲F̲T̲W̲A̲R̲E̲ ̲P̲A̲C̲K̲A̲G̲E̲



5.7.1    S̲u̲m̲m̲a̲r̲y̲ ̲o̲f̲ ̲R̲e̲q̲u̲i̲r̲e̲m̲e̲n̲t̲



5.7.1.1  P̲a̲c̲k̲a̲g̲e̲ ̲D̲e̲s̲c̲r̲i̲p̲t̲i̲o̲n̲

         The IO control SW package provides the interface between
         CAMPS application software and terminals, lines, file
         management and message management system.

         The IO control functions can be divided into two distinct
         functions:

         a)  Line interface control

         b)  Device and line control

         An overview of the IO control SW with the three main
         groups is shown in figure 5.7.1.1-1.

         The IO control software break down is shown in figure
         5.7.1.1-2.


















































                     FIGURE 5.7.1.1-1


















































                     Figure 5.7.1.1-2


5.7.1.1.1    S̲u̲m̲m̲a̲r̲y̲ ̲o̲f̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲s̲

         L̲i̲n̲e̲ ̲I̲n̲t̲e̲r̲f̲a̲c̲e̲ ̲C̲o̲n̲t̲r̲o̲l̲

         The Line Interface Control covers common software for
         interface to lines via LTUXs, LTUs, and the SSC driver.

         It is divided into:

             T̲e̲r̲m̲i̲n̲a̲l̲ ̲H̲a̲n̲d̲l̲i̲n̲g̲ ̲S̲y̲s̲t̲e̲m̲

             The Terminal Handling System controls logical channels
             to LTUXs via the TDX system and logical channels
             to the LTUs via a standard LTU handler. The THS
             supports inclusion of device/line specific handlers.

             T̲D̲X̲ ̲S̲y̲s̲t̲e̲m̲

             The TDX System provides communication on logical
             lines from the TDX driver via the TDX Host Interface
             to a number of LTUXs or other host interfaces.
             The communication is controlled by the TDX controller
             firmware.

             S̲t̲a̲n̲d̲a̲r̲d̲ ̲L̲T̲U̲ ̲H̲a̲n̲d̲l̲e̲r̲

             The standard LTU Handler provides the means for
             the Terminal Handling System to interface to LTUs
             on the IO BUS. One incarnation of the Standard
             LTU handler serves one LTU with up to 16 communication
             lines. The standard LTU Handler interfaces up to
             16 device specific Handlers.

             S̲S̲C̲ ̲D̲r̲i̲v̲e̲r̲

             The SSC Driver provides the software interface
             to the Memory MAP console interface in such a way
             that communication with the SSC Computer is supported.
             The SSC driver emulates a system console driver
             concerning on-line standard system software.



             S̲t̲a̲n̲d̲a̲r̲d̲ ̲L̲T̲U̲ ̲M̲i̲c̲r̲o̲-̲P̲r̲o̲c̲e̲s̲s̲o̲r̲ ̲S̲o̲f̲t̲w̲a̲r̲e̲

             The Standard LTU micro-processor software supports
             implementation of communication line protocol software
             in the CR8066D LTU. It is the IO Bus interface
             for data and control information input/output.

         D̲e̲v̲i̲c̲e̲ ̲&̲ ̲L̲i̲n̲e̲ ̲C̲o̲n̲t̲r̲o̲l̲

         The Device & Line Control consists of all line, channel
         and device specific software and firmware.

         It is divided into:

             N̲I̲C̲S̲ ̲T̲A̲R̲E̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The TARE control implements the level 2 interface
             of the TARE communication (i.e. the LITSYNC protocol).

             S̲C̲A̲R̲S̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The SCARS Control implements the level 2 interface
             of the SCARS communication (X25 protocol).

             C̲C̲I̲S̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The CCIS Control implements the level 2 interface
             of the CCIS communication (X25).

             T̲R̲C̲/̲T̲P̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The TRC/TP control implements the device interface
             to TRC and Teleprinter lines. This includes conversion
             to and from internal record format as well as character
             sequence recognition. ITA2/ITA5 Conversion.

             P̲T̲P̲/̲P̲T̲R̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The PTP/PTR Control implements the device interface
             to PTP/PTR. This includes conversion to and from
             internal record formats as well as character sequence
             recognition. ITA 2/5 Conversion.



             M̲e̲d̲i̲u̲m̲ ̲S̲p̲e̲e̲d̲ ̲T̲e̲l̲e̲p̲r̲i̲n̲t̲e̲r̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The Medium Speed Teleprinter control implements
             the device interface to the MSTP including conversion
             from internal record format.

             O̲C̲R̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The OCR Control implements the device interface
             to the OCR including generation of internal record
             format.

             V̲D̲U̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The VDU Control implements the device interface
             for VDUs. It consists of the format handler, VDU
             handler, and VDU LTUX firmware.

             S̲o̲f̲t̲w̲a̲r̲e̲ ̲D̲e̲v̲e̲l̲o̲p̲m̲e̲n̲t̲ ̲V̲D̲U̲ ̲C̲o̲n̲t̲r̲o̲l̲

             The Software Development VDU Control implements
             the device interface for the software development
             VDU.

             L̲i̲n̲e̲ ̲P̲r̲i̲n̲t̲e̲r̲ ̲H̲a̲n̲d̲l̲e̲r̲

             The Line Printer Handler provides the device interface
             to the line printer.

             P̲U̲-̲P̲U̲ ̲H̲a̲n̲d̲l̲e̲r̲

             The PU-PU Handler provides the interface for the
             PU-PU connection via TDX (For checkpoints).



5.7.1.1.2    S̲u̲m̲m̲a̲r̲y̲ ̲o̲f̲ ̲E̲x̲t̲e̲r̲n̲a̲l̲ ̲I̲n̲t̲e̲r̲f̲a̲c̲e̲s̲ ̲(̲F̲i̲g̲.̲ ̲5̲.̲7̲.̲1̲.̲1̲.̲2̲-̲1̲)̲

         The IO control SW interfaces to the following external
         lines (see figure).

          1) NICS TARE
          2) CCIS
          3) SCARS
          5) TRC



         and the following devices:

          4) OCR
          6) TP
          7) VDU
          8) PTP/PTR
          9) MSTP (Medicum Speed Teleprinter)
         10) LINE PRINTER
         11) SOFTWARE DEV VDU

















































                    FIGURE 5.7.1.1.2-1


5.7.1.2  P̲a̲c̲k̲a̲g̲e̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲s̲



5.7.1.2.1    L̲i̲n̲e̲ ̲I̲n̲t̲e̲r̲f̲a̲c̲e̲ ̲C̲o̲n̲t̲r̲o̲l̲

         The Line Interface Control Software interfaces the
         device control software with the CR80D computer system.

         It is the standard CR80 and microprocessor software
         providing the interface from the application to the
         line/device specific software.

         For the Processor Unit, the Terminal Handling System
         performs the overall conversion from logical line names
         to LTU or LTUX and line addresses.

         The Standard LTU handlers perform the communication
         with the LTUs located in the IO-crates and the TDX
         driver performs the communication with the LTUX connected
         to the TDX bus.

         For the LTUs, a Z80 microprocessor operating system
         and the CR80 interface software are common.

         For the TDX, the Host interface firmware, the TDX controller
         firmware, and the LTUX firmware interfacing to the
         TDX bus are independent of actual devices.

         Fig. 5.7.1.2.2-1 illustrates the Line Interface Control
         Software/Firmware as distributed in a CR80D system
         with LTUs on IO bus and LTUXs on the TDX bus.


















































                     Fig. 5.7.1.2.1-1


         T̲e̲r̲m̲i̲n̲a̲l̲ ̲H̲a̲n̲d̲l̲i̲n̲g̲ ̲S̲y̲s̲t̲e̲m̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲s̲

         The Terminal Handling System hides the physical line
         characteristics for the application. The application
         accesses lines by name.

         The SSC package defines the relationship between names
         and physical addresses, the baud rate for the external
         V24 lines, the logical linespeed, protocol/device type
         and security classifications.  Further, the SSC package
         identifies the applications to the Terminal Handling
         System (USER ON).

         The THS implements the security and access control
         for LTU and LTUX connected lines.  A request from the
         application to OPEN line is validated against the capabilities
         defined by SSC at the moment of USER ON.

         The approach is shown in fig. 5.7.1.2.1-2.

         Command exists for the SSC Package to define LTUs,
         LTUXs lines and applications.

         Command exists for the application to open and close
         channels and to perform data transfer.

         The THS supports inclusion of device specific Handlers.


















































                    FIGURE 5.7.1.2.1-2


         T̲D̲X̲ ̲S̲y̲s̲t̲e̲m̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         The TDX system performs multiplexed data transfers
         (logical lines) between the two processor units and
         between the processor units and up to 242 LTUXs. It
         transfers up to 819200 bps. on max. 4096 logical lines.

         The transmission on the TDX bus is controlled by the
         TDX controller. In the processor unit the TDX Driver
         is the interface to the TDX Host Interface.

         Figure 5.7.1.2.1-3 illustrates the TDX system.



















































                    FIGURE 5.7.1.2.1-3


         L̲T̲U̲X̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲ ̲a̲n̲d̲ ̲I̲n̲t̲e̲r̲f̲a̲c̲e̲

         The LTUX is the standard interface between the TDX
         Bus and terminals e.g. VDU, PTP, and OCR. At the TDX
         side the TDX packet protocol is used for data transport.

         The smallest unit, with which the unit works, is a
         TDX frame. A frame contains one protocol byte, a three
         bit sequence number, five bit byte counts and up to
         sixteen data bytes. (Extended HDLC protocol with CRC
         check). A TDX packet may contain several frames. The
         frames are numbered contiguously (module 8) in order
         to ensure correct transmission.

         Each LTUX interfaces to four CCITT V24/V28 external
         lines and is able to handle ITA no. 2 and no. 5. The
         maximum transmission speed on the external lines are
         4 x 2400 bps. or 1 x 9600 bps.

         The TDX Controller multiplexes the data stream on the
         TDX bus in a way to allow a logical line transmission
         speed up to 819200 bps. (this number depends on the
         firmware configuration in the LTUX).

         Each LTUX is able to interface up to 16 logical lines
         by multiplexing the data stream from/to the TDX bus.

         A possible allocation of logical lines to physical
         lines is shown in fig. 5.7.1.2.1-4 for VDUs.

         T̲D̲X̲ ̲H̲o̲s̲t̲ ̲I̲n̲t̲e̲r̲f̲a̲c̲e̲

         All traffic between a processor unit and the TDX bus
         are executed by the TDX Host Interface.

         The Host Interface is a high band width device that
         interface directly to the CR80D main bus.

         T̲D̲X̲ ̲C̲o̲n̲t̲r̲o̲l̲l̲e̲r̲

         The traffic on the TDX bus is controlled by the TDX
         Controller.

         The Controller receives all frames transmitted from
         the Host Interface and LTUXs, executes CRC check and
         retransmit the frames.

         The main task for the TDX Controller is to control
         the transmission speeds allocated by SSC for each TDX
         device.



















































                     Fig. 5.7.1.2.1-4


         T̲D̲X̲ ̲E̲r̲r̲o̲r̲ ̲H̲a̲n̲d̲l̲i̲n̲g̲

         All errors included CRC and missing frames will result
         in rejection of the complete packet immediately, without
         waiting for completion of the packet. The receiving
         device then requests a retransmission by replying NAK
         (Negative Acknowledgement). Also the acknowledgement
         sent to the transmitting device is checked for errors.

         A TDX system error and switch over is handled by the
         IOC and SSC in common. The watchdog continuously checks
         the TDX-Controller clock and advices SSC in case of
         error.

         S̲t̲a̲n̲d̲a̲r̲d̲ ̲L̲T̲U̲ ̲H̲a̲n̲d̲l̲e̲r̲s̲

         The Standard LTU Handlers perform the communication
         to the LTUs located on the IO BUS. One incarnation
         of the Handler services one LTU.

         The Handler interfaces to the terminal handling system
         receiving request herefrom. Figure 5.7.1.2.1-5 illustrates
         the approach.




















































                    FIGURE 5.7.9.2.2-5


         S̲t̲a̲n̲d̲a̲r̲d̲ ̲L̲T̲U̲ ̲M̲i̲c̲r̲o̲ ̲P̲r̲o̲c̲e̲s̲s̲o̲r̲ ̲S̲o̲f̲t̲w̲a̲r̲e̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲s̲

         The Standard LTU micro processor software provides
         the environment for the protocol software.

         a)  it provides LTU initialization

         b)  it provides LTU on-line diagnostics

         c)  it provides a micro processor operating system
             for executing protocol software

         d)  it provides pool management for buffers

         e)  it provides a standard queue interface to the CR80D
             processor unit

         f)  it provides V24 drivers

         The concept is shown in figure 5.7.1.2.1-6.




















































                    Figure 5.7.1.2.2-6


5.7.1.2.2    D̲e̲v̲i̲c̲e̲ ̲a̲n̲d̲ ̲L̲i̲n̲e̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲s̲

         The Device and Line Control Functions are the functions
         supporting specific devices and line protocols.

         In this section the device/line functions are outlined
         for each device/line.  In fig. 5.7.1.2 2-1 an overview
         of interface, speed, alphabet and protocols is presented.
          At the end of this section the Internal Message Record
         Format is shown.

         N̲I̲C̲S̲ ̲T̲A̲R̲E̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         Ref.:  CPS/ICD/004.

         The control function implements the level 2 interface.

         The protocol description is given in the document:

         "TARE synchronous channel protocol performance specifications",
         no. 177000-600, version F, 29th June 1979, updated
         with DCN G 2 of 15th February 1980.

         S̲C̲A̲R̲S̲/̲C̲C̲I̲S̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         Ref.: Interface Specification CAMPS/SCARS II/ACCIS
         of 18 July 1980.

         T̲R̲C̲,̲ ̲P̲o̲i̲n̲t̲ ̲t̲o̲ ̲P̲o̲i̲n̲t̲ ̲C̲o̲n̲n̲e̲c̲t̲i̲o̲n̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         Ref.:  CPS/ICD/007

         O̲C̲R̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         Ref.:  CPS/ICD/008

         The transmission is in blocks of upto 512 bytes.

         The OCR uses the following sparator marks:

         SEP-(SP)-                       separate works, variable
                                         separator

         EOL-(CR)(LF)-                   separate text lines

         EOLF-(CR)(CR)(LF)-              separate format lines



         It shall be possible to close and open for message
         traffic from the OCR by use of circuit V24-106.

         In case of parity check error and format error the
         message will be sent for message service.

         CAMPS control the OCR mode and the block transmission
         from the OCR.

         The following control characters in Nato 7-bit code
         are used.

         DC1     Device Control 1
         DC3     Device Control 3
         STX     Start of Text
         ETB     End of Transmission Block
         ETX     End of Text
         ACK     Acknowledge
         NAK     Negative Acknowledge

         D̲C̲1 - sent from CAMPS, controlled by the supervisor.
          The OCR must not transmit before DC1 is received.

         D̲C̲3̲ - sent from CAMPS, controlled by the supervisor.
          The OCR must not transmit when a DC3 is received.
          The V24-108/2 is switched to the logical low level.

         S̲T̲X̲ - sent to CAMPS.
         Indicates that a message is ready for transmission.

         E̲T̲B̲ - sent to CAMPS.
         ETB is a block separator sent after each 512 byte block.

         E̲T̲X̲ - sent to CAMPS.
         ETX is a message separator sent after the last data
         byte.

         A̲C̲K̲ - sent from CAMPS.
         This character indicates that the last data block is
         received and that CAMPS is ready to receive the next
         block or the STX character.

         N̲A̲K̲ - sent from CAMPS.
         NAK indicates that the last received block or control
         character is not accepted.



         T̲e̲l̲e̲p̲r̲i̲n̲t̲e̲r̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         The teleprinter configuration includes a paper tape
         reader/puncher. The SSC decides the Teleprinter function.

         Each teleprinter channel is opened and closed by the
         SSC software.

         P̲T̲P̲/̲P̲T̲R̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         The PTP/PTR configuration includes a physical security
         key on the PTR.  The SSC specifies whether PTP and
         PTR are ready for punch/read.

         M̲e̲d̲i̲u̲m̲ ̲S̲p̲e̲e̲d̲ ̲T̲e̲l̲e̲p̲r̲i̲n̲t̲e̲r̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         The medium speed teleprinter is a ROP device with paper
         out control and physical security key.

         V̲D̲U̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         The communication method is block mode transmission.
         The electrical interface is as specified in fig. 5.7.1.2.2-2.
         Baud rates are 1200 and 2400 bps.

         A̲p̲p̲l̲i̲c̲a̲t̲i̲o̲n̲ ̲S̲o̲f̲t̲w̲a̲r̲e̲ ̲I̲n̲t̲e̲r̲f̲a̲c̲e̲ ̲t̲o̲ ̲V̲D̲U̲.

         The application S/W interfaces to the VDU on split
         basis.

         The VDU screen is divided into two splits:

         VDU header area - split #0
         VDU format area - split #1

         VDU Format Area

         The format area consists of a number of lines. If the
         number of lines is greater than the displayed format
         area (22 lines) the user may page or scroll to see
         the rest.



         The maximum size of the split is 44 lines.

                    ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲

                        VDU SPLIT

               ----------------------------

                         PRESENT DISPLAYED            VDU
                            FORMAT AREA              SCREEN

               ----------------------------

                                                     SCROLL
 
                                                      



                   ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲ ̲
                             
                      SPLIT CONCEPT


         A split consists of protected and unprotected fields
         in any order. When the VDU is in format mode the user
         is able to write and update within the unprotected
         fields. On transmit request, only the contents of the
         unprotected fields is sent to the application. The
         application is able to select which fields to be transmitted
         from the VDU.

         Addressing

         The fields in both splits are addressed by line type
         numbers, incarnation numbers and field numbers. A group
         of repeatable lines have the same line type number,
         but different incarnation number.

         Line type, Incarnation         Field No.

         1,1                            1̲ ̲ 2̲ ̲ ̲ ̲ ̲ ̲ ̲ 3̲ ̲ ̲ ̲ ̲ ̲
         1,2                            1̲ ̲ 2̲ ̲ ̲ ̲ ̲ ̲ ̲ 3̲ ̲ ̲ ̲ ̲ ̲
         2,1                            1̲ ̲ 2̲ ̲ ̲ ̲ ̲ 3̲ ̲ ̲ 4̲ ̲ ̲ ̲
         3,1                            1̲ ̲ 2̲ ̲ ̲ ̲ ̲ ̲ ̲ 3̲ ̲ ̲ ̲ ̲ ̲
         3,2                            1̲ ̲ 2̲ ̲ ̲ ̲ ̲ ̲ ̲ 3̲ ̲ ̲ ̲ ̲ ̲

                     
                                            VDU SCREEN


                LINE AND FIELD ADDRESSING

         F̲o̲r̲m̲a̲t̲ ̲H̲a̲n̲d̲l̲e̲r̲

         The Format Handler uses the format definitions to build
         up empty or filled out standard formats on the VDU
         screen.

         The format definition resides in a format file. They
         are fixed at system generation and contain information
         about the different standard formats used by CAMPS.

         The format definitions are maintained by the Offline
         Package at the CSSI site.

         The Format Handler keeps track on the different types
         of lines in the present format and the number of lines.

         A̲p̲p̲l̲i̲c̲a̲t̲i̲o̲n̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲s̲

         The application functions listed below are given names
         relative to their function, however, these names may
         be redefined.



         D̲e̲f̲i̲n̲e̲ ̲F̲o̲r̲m̲a̲t̲ ̲A̲r̲e̲a̲

         This command defines the system format area to be used
         in the VDU communication. The application may communicate
         with more than one VDU and thus need a larger format
         area than an application communicating with one VDU.

         D̲e̲f̲i̲n̲e̲ ̲F̲o̲r̲m̲a̲t̲ ̲F̲i̲l̲e̲

         This command defines to the system which format file
         shall be used. Formats are obtained from this file
         by the Get Format command.

         G̲e̲t̲ ̲F̲o̲r̲m̲a̲t̲

         This command prepares the specified format for modification
         by insert lines and delete lines below as well as output
         by Output Format.

         O̲u̲t̲p̲u̲t̲ ̲F̲o̲r̲m̲a̲t̲

         This command outputs the format obtained by Get Format
         and modified as of insert and delete line. The page
         now contains the text in the format with all fields
         blank.

         F̲i̲e̲l̲d̲s̲ ̲O̲u̲t̲p̲u̲t̲

         Fields are assumed organized as a consecutive sequence
         of records in a buffer. In parallel a list of field
         identifiers (line type, incarnation, field number)
         shall be specified. The Field Output function moves
         the first record to the first field in the list, the
         second to the second, etc.

         F̲i̲e̲l̲d̲s̲ ̲I̲n̲p̲u̲t̲

         The Fields Input function inputs the requested number
         of fields from and including the field specified as
         the first. The field content is returned as records
         in the way that trailing blanks within the records
         are omitted. If the buffer specified is not sufficiently
         long the input is terminated when the buffer is full.

         Note that fields are not input upon depression of ENTER,
         or RETURN, but that these keys are returned to the
         application, which will reserve a buffer and request
         the transmission. 



         R̲e̲c̲e̲i̲v̲e̲ ̲C̲o̲n̲t̲r̲o̲l̲

         Function keys destined for the application (All except
         the key giving system attention) are received when
         the Receive Control function is requested (pending
         read).

         S̲e̲n̲d̲ ̲C̲o̲n̲t̲r̲o̲l̲

         Control characters are transmitted to the VDU by this
         function. An example is Bell.

         C̲h̲a̲n̲g̲e̲ ̲F̲i̲e̲l̲d̲ ̲A̲t̲t̲r̲i̲b̲u̲t̲e̲s̲

         If a field has been defined with changeable attributes,
         they may be modified by this command. The attributes
         are modified from the previous value to the specified
         e.g. intensity change, flash.

         I̲n̲s̲e̲r̲t̲ ̲L̲i̲n̲e̲s̲

         This command inserts the specified number of lines
         as incarnation of the specified line type. Calling
         the specified incarnation N, the lines will be inserted
         as incarnation N, N+1.... Insert Lines is allowed up
         to the size of a split.

         D̲e̲l̲e̲t̲e̲ ̲L̲i̲n̲e̲s̲

         This command deletes the specified number of lines
         from the incarnations of lines for the specified line
         type calling the specified incarnation N incarnations
         N, N+1.... will be deleted.

         Insert Lines and Delete Lines have effect to redefine
         the format obtained by Get Format and will have no
         immediate effect on the VDU as long as Output Format
         has not been executed. After Output Format the Insert
         Lines imply an immediate shift-down of the lines on
         the VDU and the Delete Lines an immediate shift-up
         of lines on the VDU.
















































                     Fig. 5.7.1.2.2-1


                N̲o̲t̲e̲s̲ ̲t̲o̲ ̲F̲i̲g̲.̲ ̲5̲.̲7̲.̲1̲.̲2̲.̲2̲-̲1̲

         1)  EDC-Protocol          As defined in CPS/230/ICD/0004

         2)  LAP Protocol          As defined in CPS/230/ICD/0006

         3)  Baud Rate             Underlined baud-rates shall
                                   not be exceeded during test.

         4)  Crypto I/F            Interface to DOLCE as defined
                                   in CPS/230/ICD/0004.

         5)  10 bit code            character-by-character with
                                   odd parity.  Start bit, 7
                                   data bit, parity bit, and
                                   one stop bit.

         6)  7 bit code            Start bit, 5 data bits and
                                   stop bit.

         7)                        Refer IO Control Preliminary
                                   Design.

















































                 Figs. 5.7.1.2.2-2 og -3



         M̲e̲s̲s̲a̲g̲e̲ ̲R̲e̲c̲o̲r̲d̲ ̲F̲o̲r̲m̲a̲t̲

         All incoming information is converted from the various
         types of formats, used by the external equipment, to
         a standard message record format. This record format
         is again converted to the proper formats when information
         is transmitted to the external equipment.

         The ITA no. 5 code is used. The records are separated
         by a record separator.

         After the record separator is a character count byte.
         

         The byte before the text string is kept open for purposes
         not yet defined.


















































                    FIGURE 5.7.1.2.2-4


         S̲o̲f̲t̲w̲a̲r̲e̲ ̲D̲e̲v̲e̲l̲o̲p̲m̲e̲n̲t̲ ̲V̲D̲U̲ ̲C̲o̲n̲t̲r̲o̲l̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         The Software Development VDU is interfaced according
         to requirements from support software. The VDU communication
         is TTY mode.

         L̲i̲n̲e̲ ̲P̲r̲i̲n̲t̲e̲r̲ ̲H̲a̲n̲d̲l̲e̲r̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲

         Refer IO Control Preliminary design.

         P̲U̲-̲P̲U̲ ̲H̲a̲n̲d̲l̲e̲r̲

         The PU-PU Handler handles the communication from PU
         to PU via TDX.

         P̲h̲y̲s̲i̲c̲a̲l̲ ̲S̲e̲c̲u̲r̲i̲t̲y̲ ̲K̲e̲y̲

         On each VDU, medium speed teleprinter, and the PTP
         is there a physical locking key. A terminal is activated
         by turning the locking key to "ON". This indicates
         whether the terminal is manned or unmanned.

         S̲S̲C̲ ̲D̲r̲i̲v̲e̲r̲ ̲F̲u̲n̲c̲t̲i̲o̲n̲s̲

         The SSC Driver supports Processor unit interface to
         the SSC compatible with TP.

         Line Speed 9600 baud
         Printed line with 69 characters
         No Echo of input characters

         V24 lines are as defined for the MAP (Refer section
         5.1.4.1.4).



5.7.1.3  P̲a̲c̲k̲a̲g̲e̲ ̲C̲o̲n̲t̲r̲o̲l̲

         I̲n̲i̲t̲i̲a̲l̲i̲z̲a̲t̲i̲o̲n̲

         The IO Control SW is initialized by the SSC Package
         in two steps. The PU resident software is loaded with
         the system software at time of Bootload.

         The Protocol microprocessor software in the LTUs is
         loaded when the lines served are defined.



         E̲r̲r̲o̲r̲ ̲H̲a̲n̲d̲l̲i̲n̲g̲

         Errors not handled by the application are returned
         to the SSC SW.

         For further information please refer to sec. 4.11.





5.7.1.4  C̲h̲a̲r̲a̲c̲t̲e̲r̲i̲s̲t̲i̲c̲s̲

         Refer CPS/210/SYS/0001 section 3.4.1.



5.7.1.5  D̲e̲s̲i̲g̲n̲ ̲a̲n̲d̲ ̲C̲o̲n̲s̲t̲r̲u̲c̲t̲i̲o̲n̲

         Refer to section 2.5.



5.7.1.6  D̲o̲c̲u̲m̲e̲n̲t̲a̲t̲i̲o̲n̲

         Refer to section 2.6.



5.7.2    E̲n̲v̲i̲r̲o̲n̲m̲e̲n̲t̲



5.7.2.1  S̲t̲a̲n̲d̲a̲r̲d̲ ̲H̲a̲r̲d̲w̲a̲r̲e̲,̲ ̲F̲i̲r̲m̲w̲a̲r̲e̲,̲ ̲a̲n̲d̲ ̲S̲o̲f̲t̲w̲a̲r̲e̲

         N.A.



5.7.2.2  E̲x̲t̲e̲r̲n̲a̲l̲ ̲I̲n̲t̲e̲r̲f̲a̲c̲e̲s̲

         The external interface is an integrated part of IOC
         functions, refer to section 5.7.1.2.3.



5.7.2.3  S̲u̲b̲s̲y̲s̲t̲e̲m̲ ̲I̲n̲t̲e̲r̲f̲a̲c̲e̲s̲

         a)  CR80D Subsystem

             The IO control SW executes partly in the processor
             units (refer fig. 5.7.1.2.2-1)

         b)  Kernel Subsystem. The IO Control SW uses the following
             Kernel Functions:

             Process communication, scheduling, security.

             Data transfer by low level Handlers.



         c)  Storage & File Management

             The IOC interfaces to SFM for read of VDU formats
             of the format file.

         d)  SSC SW

             The SSC SW controls the IO control SW.

         e)  Other applications and system software packages

             These packages interface to the IO Control SW as